If a transformer is banked and connected wye on the low side, what system voltage would it yield?

Enhance your skills with our 3rd Year Lineman Apprentice Exam. Master the essentials with interactive materials, flashcards, and insightful explanations to boost your confidence and readiness.

When determining the system voltage yielded by a transformer that is banked and connected in a wye configuration on the low side, it is important to understand the relationship between line voltage and phase voltage in a wye system. In a wye connection, the line voltage is equal to the square root of three (√3) times the phase voltage.

In typical scenarios where transformers are used, the low side voltage for a wye-connected transformer is often specified in terms of line-to-neutral voltage rather than line-to-line voltage. For example, the 4160-volt system typically refers to a configuration where the line-to-line voltage measures 4160 volts, making the phase voltage approximately 2400 volts (4160 volts / √3).

The given choice of 4160 volts 3-phase 4-wire indicates both the three-phase aspect and the presence of a neutral wire that is typically used in wye systems, allowing for the dual capability of providing both single-phase and three-phase power. This is commonly seen in distribution systems involving transformers that are designed to supply a mix of load types.

The other choices present different voltage levels and configurations, but the choice of 4160 volts best matches the standardized configuration that's commonly seen in the field